The ultimate purpose of MAAS is to deploy and manage machines. As explained in About the machine life-cycle, machines must first be enlisted or commissioned, then acquired, then deployed. This article will tell you:

How to commission a machine

Note that if you are using your own commissioning scripts, and you do not want them to automatically run every time, you must specify noauto, as in this script snippet:

#!/bin/bash
#
# --- Start MAAS 1.0 script metadata ---
# name: 50-dummy-example
# title: Dummy example
# description: Just an example
# script_type: commissioning
# tags: noauto

If you do not specify noauto, your custom commissioning scripts will run every time commissioning is attempted.

To commission a machine:

  1. Go to the “Machines” page.

  2. Select the machine(s) you want to commission.

  3. Choose “Commission” under the “Take action” drop-down menu:

You have the option of selecting some extra parameters (checkboxes) and performing hardware tests.

These options include:

  • Allow SSH access and prevent machine powering off: Machines are normally powered off after commissioning. This option keeps the machine on and enables SSH so you can access the machine.

  • Retain network configuration: When enabled, preserves any custom network settings previously configured for the machine. See Networking for more information.

  • Retain storage configuration: When enabled, preserves any storage settings previously configured for the machine. See Storage for more details.

  • Update firmware: Runs scripts tagged with update_firmware.

  • Configure HBA: Runs scripts tagged with configure_hba.

  1. Click the Hardware tests field to reveal a drop-down list of tests to add and run during commissioning. See Hardware testing for more information on hardware testing scripts.

  2. Finalise the directive by hitting “Commission machine”.

While commissioning, the machine status will change to reflect this state (Commissioning). MAAS discovers the machine’s network topology. MAAS then prompts a machine network interface to connect to the fabric, VLAN, and subnet combination for configuration. Usually, MAAS assigns a static IP address out of the reserved IP range for the subnet (“Auto assign” mode). The next section details several assignment modes.

Once commissioned, a machine’s status will change to Ready, and an extra tab for the machine called “Commissioning” will become available. This tab contains the results of the scripts executed during the commissioning process.

To commission a machine that’s in the “Ready” state, via the CLI, use the following command:

maas $PROFILE machine commission $SYSTEM_ID
Typical JSON output (long listing)
Success.
Machine-readable output follows:
{
    "storage_test_status_name": "Pending",
    "bcaches": [],
    "cpu_count": 1,
    "interface_set": [
        {
            "params": "",
            "numa_node": 0,
            "tags": [],
            "id": 10,
            "mac_address": "52:54:00:15:36:f2",
            "vendor": "Red Hat, Inc.",
            "children": [],
            "effective_mtu": 1500,
            "discovered": [],
            "links": [],
            "link_speed": 0,
            "link_connected": true,
            "system_id": "bhxws3",
            "enabled": true,
            "interface_speed": 0,
            "firmware_version": null,
            "name": "ens3",
            "sriov_max_vf": 0,
            "product": null,
            "vlan": {
                "vid": 0,
                "mtu": 1500,
                "dhcp_on": true,
                "external_dhcp": null,
                "relay_vlan": null,
                "fabric": "fabric-2",
                "primary_rack": "8dwnne",
                "name": "untagged",
                "id": 5003,
                "space": "undefined",
                "secondary_rack": null,
                "fabric_id": 2,
                "resource_uri": "/MAAS/api/2.0/vlans/5003/"
            },
            "parents": [],
            "type": "physical",
            "resource_uri": "/MAAS/api/2.0/nodes/bhxws3/interfaces/10/"
        }
    ],
    "network_test_status_name": "Unknown",
    "numanode_set": [
        {
            "index": 0,
            "memory": 985,
            "cores": [
                0
            ]
        }
    ],
    "locked": false,
    "hardware_uuid": "F677A842-571C-4E65-ADC9-11E2CF92D363",
    "default_gateways": {
        "ipv4": {
            "gateway_ip": null,
            "link_id": null
        },
        "ipv6": {
            "gateway_ip": null,
            "link_id": null
        }
    },
    "status_action": "",
    "status_message": "Commissioning",
    "cpu_test_status_name": "Unknown",
    "memory_test_status": -1,
    "virtualblockdevice_set": [],
    "pool": {
        "name": "default",
        "description": "Default pool",
        "id": 0,
        "resource_uri": "/MAAS/api/2.0/resourcepool/0/"
    },
    "current_testing_result_id": 9,
    "current_installation_result_id": null,
    "netboot": true,
    "description": "",
    "special_filesystems": [],
    "testing_status": 0,
    "memory": 1024,
    "current_commissioning_result_id": 8,
    "storage": 5368.70912,
    "commissioning_status": 0,
    "cpu_test_status": -1,
    "tag_names": [
        "virtual"
    ],
    "memory_test_status_name": "Unknown",
    "swap_size": null,
    "status_name": "Commissioning",
    "other_test_status": -1,
    "pod": null,
    "storage_test_status": 0,
    "blockdevice_set": [
        {
            "id_path": "/dev/disk/by-id/ata-QEMU_HARDDISK_QM00001",
            "size": 5368709120,
            "block_size": 512,
            "tags": [
                "ssd"
            ],
            "serial": "QM00001",
            "uuid": null,
            "numa_node": 0,
            "available_size": 5368709120,
            "id": 3,
            "partition_table_type": null,
            "model": "QEMU HARDDISK",
            "path": "/dev/disk/by-dname/sda",
            "storage_pool": null,
            "used_for": "Unused",
            "filesystem": null,
            "system_id": "bhxws3",
            "used_size": 0,
            "partitions": [],
            "name": "sda",
            "type": "physical",
            "resource_uri": "/MAAS/api/2.0/nodes/bhxws3/blockdevices/3/"
        }
    ],
    "other_test_status_name": "Unknown",
    "distro_series": "",
    "testing_status_name": "Pending",
    "ip_addresses": [],
    "address_ttl": null,
    "system_id": "bhxws3",
    "physicalblockdevice_set": [
        {
            "firmware_version": "2.5+",
            "serial": "QM00001",
            "uuid": null,
            "numa_node": 0,
            "available_size": 5368709120,
            "size": 5368709120,
            "tags": [
                "ssd"
            ],
            "id": 3,
            "partition_table_type": null,
            "id_path": "/dev/disk/by-id/ata-QEMU_HARDDISK_QM00001",
            "model": "QEMU HARDDISK",
            "path": "/dev/disk/by-dname/sda",
            "storage_pool": null,
            "used_for": "Unused",
            "filesystem": null,
            "system_id": "bhxws3",
            "used_size": 0,
            "partitions": [],
            "name": "sda",
            "block_size": 512,
            "type": "physical",
            "resource_uri": "/MAAS/api/2.0/nodes/bhxws3/blockdevices/3/"
        }
    ],
    "fqdn": "ace-swan.maas",
    "osystem": "",
    "domain": {
        "authoritative": true,
        "ttl": null,
        "resource_record_count": 0,
        "name": "maas",
        "id": 0,
        "is_default": true,
        "resource_uri": "/MAAS/api/2.0/domains/0/"
    },
    "boot_interface": {
        "params": "",
        "numa_node": 0,
        "tags": [],
        "id": 10,
        "mac_address": "52:54:00:15:36:f2",
        "vendor": "Red Hat, Inc.",
        "children": [],
        "effective_mtu": 1500,
        "discovered": [],
        "links": [],
        "link_speed": 0,
        "link_connected": true,
        "system_id": "bhxws3",
        "enabled": true,
        "interface_speed": 0,
        "firmware_version": null,
        "name": "ens3",
        "sriov_max_vf": 0,
        "product": null,
        "vlan": {
            "vid": 0,
            "mtu": 1500,
            "dhcp_on": true,
            "external_dhcp": null,
            "relay_vlan": null,
            "fabric": "fabric-2",
            "primary_rack": "8dwnne",
            "name": "untagged",
            "id": 5003,
            "space": "undefined",
            "secondary_rack": null,
            "fabric_id": 2,
            "resource_uri": "/MAAS/api/2.0/vlans/5003/"
        },
        "parents": [],
        "type": "physical",
        "resource_uri": "/MAAS/api/2.0/nodes/bhxws3/interfaces/10/"
    },
    "hostname": "ace-swan",
    "network_test_status": -1,
    "min_hwe_kernel": "",
    "power_state": "off",
    "interface_test_status_name": "Unknown",
    "owner_data": {},
    "volume_groups": [],
    "power_type": "virsh",
    "node_type": 0,
    "owner": "admin",
    "cache_sets": [],
    "architecture": "amd64/generic",
    "hwe_kernel": null,
    "zone": {
        "name": "default",
        "description": "",
        "id": 1,
        "resource_uri": "/MAAS/api/2.0/zones/default/"
    },
    "disable_ipv4": false,
    "boot_disk": {
        "firmware_version": "2.5+",
        "serial": "QM00001",
        "uuid": null,
        "numa_node": 0,
        "available_size": 5368709120,
        "size": 5368709120,
        "tags": [
            "ssd"
        ],
        "id": 3,
        "partition_table_type": null,
        "id_path": "/dev/disk/by-id/ata-QEMU_HARDDISK_QM00001",
        "model": "QEMU HARDDISK",
        "path": "/dev/disk/by-dname/sda",
        "storage_pool": null,
        "used_for": "Unused",
        "filesystem": null,
        "system_id": "bhxws3",
        "used_size": 0,
        "partitions": [],
        "name": "sda",
        "block_size": 512,
        "type": "physical",
        "resource_uri": "/MAAS/api/2.0/nodes/bhxws3/blockdevices/3/"
    },
    "status": 1,
    "iscsiblockdevice_set": [],
    "raids": [],
    "node_type_name": "Machine",
    "hardware_info": {
        "system_vendor": "QEMU",
        "system_product": "Standard PC (i440FX + PIIX, 1996)",
        "system_family": "Unknown",
        "system_version": "pc-i440fx-focal",
        "system_sku": "Unknown",
        "system_serial": "Unknown",
        "cpu_model": "Intel Core Processor (Skylake, IBRS)",
        "mainboard_vendor": "Unknown",
        "mainboard_product": "Unknown",
        "mainboard_serial": "Unknown",
        "mainboard_version": "Unknown",
        "mainboard_firmware_vendor": "SeaBIOS",
        "mainboard_firmware_date": "04/01/2014",
        "mainboard_firmware_version": "1.13.0-1ubuntu1",
        "chassis_vendor": "QEMU",
        "chassis_type": "Other",
        "chassis_serial": "Unknown",
        "chassis_version": "pc-i440fx-focal"
    },
    "commissioning_status_name": "Pending",
    "bios_boot_method": "pxe",
    "interface_test_status": -1,
    "cpu_speed": 0,
    "resource_uri": "/MAAS/api/2.0/machines/bhxws3/"
}

If you need to find the machine’s $SYSTEM_ID, you can use a command like this one:

maas $PROFILE machines read | jq '.[] | .hostname, .system_id'
"ace-swan"
"bhxws3"

Once commissioned, you may consider adding a tag to this machine. The next step is testing and deployment.

How to test machines

This section explains:

You can also refer to technical details and examples for commissioning scripts and testing scripts as needed.

How to download built-in scripts

You can download the source for all commissioning and test scripts via the API with the following command:

maas $PROFILE node-script download $SCRIPT_NAME

The source code to all built-in scripts is available on launchpad.

How to upload scripts

Scripts can be uploaded to MAAS using the web UI. Select the ‘User scripts’ tab of the ‘Settings’ page - the ‘Commissioning scripts’ section is near the top. Within the Commissioning scripts section, click the Upload script button followed by ‘Choose file’ to open a requester, locate the script, and select Upload to upload it to MAAS.

A status message of Commissioning script created will appear. You’ll then be able to select your script after selecting Test hardware from a machine’s ‘Take action’ menu.

MAAS executes scripts in lexicographical order. This order allows you to control when your scripts execute, and whether they run before or after the standard MAAS scripts.

How to debug script failures

Clicking on the title of a completed or failed script will reveal the output from that specific script.

If you need further details, especially when writing and running your own scripts, you can connect to a machine and examine its logs and environment.

To do this, enable Allow SSH access and prevent the machine from powering off when selecting ‘Test hardware’ from the machine ‘Take action’ menu.

Because scripts operate within an ephemeral version of Ubuntu, enabling this option stops the machine from shutting down, allowing you to connect and probe a script’s status.

As long as you’ve added your SSH key to MAAS, you can connect with SSH to the machine’s IP with a username of ubuntu. Type sudo -i to get root access.

How to upload hardware testing scripts

To upload a hardware testing script to MAAS, enter the following:

maas $PROFILE node-scripts create name=$SCRIPT_NAME name> \
 script=$PATH_TO_SCRIPT type=testing

Changing the type to commissioning adds the test script to the commissioning process.

How to list all uploaded hardware testing scripts

You can list all uploaded scripts with the following command:

maas $PROFILE node-scripts read type=testing filters=$TAG

The optional filters argument lets you search for tags assigned to a script, such as using TAG=cpu with the above example.

How to update hardware testing scripts

A script’s metadata, and even the script itself, can be updated from the command line:

maas $PROFILE node-script update \
 $SCRIPT_NAME script=$PATH_TO_SCRIPT comment=$COMMENT

The JSON formatted output to the above command will include ‘history’ dictionary entries, detailing script modification times and associated comments:

"history": [
    {
        "id": 40,
        "created": "Tue, 12 Sep 2017 12:12:08 -0000",
        "comment": "Updated version"
    },
    {
        "id": 34,
        "created": "Fri, 08 Sep 2017 17:07:46 -0000",
        "comment": null
    }
]

How to revert hardware testing scripts

MAAS keeps a history of all uploaded script versions, allowing you to easily revert to a previous version, using the id of the desired version:

maas $PROFILE node-script revert $SCRIPT_NAME to=$VERSION_ID

Warning: The history for later modifications will be lost when reverting to an earlier version of the script.

How to download a script

To download a script, enter the following:

maas $PROFILE node-script download $SCRIPT_NAME > $LOCAL_FILENAME

How to delete a script

To delete a script, use delete:

maas $PROFILE node-script delete $SCRIPT_NAME

How to view script results

The command line allows you to not only view the current script’s progress but also retrieve the verbatim output from any previous runs too.

If you only want to see the latest or currently-running result, you can use current-commissioning, current-testing, or current-installation instead of an id:

maas $PROFILE node-script-result read $SYSTEM_ID $RESULTS

How to filter script results

You can also limit which results are returned by type (commissioning, testing, or installation), script name, or script run:

maas $PROFILE node-script-results read \
 $SYSTEM_ID type=$SCRIPT_TYPE filters=$SCRIPT_NAME,$TAGS

How to suppress failed results

You can also suppress failed results, which is useful if you want to ignore a known failure:

maas $PROFILE node-script-results update \
 $SYSTEM_ID type=$SCRIPT_TYPE filters=$SCRIPT_NAME,$TAGS suppressed=$SUPPRESSED

where $SUPPRESSED is either True or False. The JSON formatted output to the above command will include ‘results’ dictionary with an entry for suppressed:

"results": [
    {
        "id": 21,
        "created": "Tue, 02 Apr 2019 17:00:36 -0000",
        "updated": "Tue, 02 Apr 2019 20:56:41 -0000",
        "name": "smartctl-validate",
        "status": 5,
        "status_name": "Aborted",
        "exit_status": null,
        "started": "Tue, 02 Apr 2019 20:56:41 -0000",
        "ended": "Tue, 02 Apr 2019 20:56:41 -0000",
        "runtime": "0:00:00",
        "starttime": 1554238601.765214,
        "endtime": 1554238601.765214,
        "estimated_runtime": "0:00:00",
        "parameters": {
            "storage": {
                "argument_format": "{path}",
                "type": "storage",
                "value": {
                    "id_path": "/dev/vda",
                    "model": "",
                    "name": "sda",
                    "physical_blockdevice_id": 1,
                    "serial": ""
                }
            }
        },
        "script_id": 1,
        "script_revision_id": null,
        "suppressed": true
    }
]

Finally, results can be downloaded, either to stdout, stderr, as combined output or as a tar.xz:

maas $PROFILE node-script-result download $SYSTEM_ID $RUN_ID output=all \
 filetype=tar.xz > $LOCAL_FILENAME

$RUN_ID is labelled id in the verbose result output.

How to locate script files

Commissioning and testing script files may be found in the following directories:

  1. /tmp/user_data.sh.*/scripts/commissioning/: Commissioning scripts
  2. /tmp/user_data.sh.*/scripts/testing/: Hardware testing scripts

How to locate log files

Commissioning and testing log files may be found in the following directories:

  1. /tmp/user_data.sh*/out/
  2. /var/log/cloud-init-output.log
  3. /var/log/cloud-init.log

How to run all scripts manually

You can also run all commissioning and hardware-testing scripts on a machine for debugging.

/tmp/user_data.sh.*/bin/maas-run-remote-scripts \
    [--no-download] \
    [--no-send] \
    /tmp/user_data.sh.*

Where:

  1. --no-download: Optional. Do not download the scripts from MAAS again.
  2. --no-send: Optional. Do not send the results to MAAS.

For example, to run all the scripts again without downloading again from MAAS:

/tmp/user_data.sh.*/bin/maas-run-remote-scripts --no-download /tmp/user_data.sh.*

Here, all the scripts are run again after downloading from MAAS, but no output data is sent to MAAS:

/tmp/user_data.sh.*/bin/maas-run-remote-scripts --no-send /tmp/user_data.sh.*

How to apply a hardware test

To launch a test, select the target machine from the ‘Machines’ page and use the ‘Take action’ drop-down menu to select ‘Test hardware’. When ready, hit the ‘Test machine’ button. Here, a test is applied to a deployed machine:

There is the option of not powering off the machine and to allow SSH access.

A default test will be selected (smartctl-validate, a hard drive test) but you can choose others by clicking the ‘Select scripts’ label. Doing so will reveal the following choices:

See Commissioning Scripts Reference for more details on how these scripts work and how you can write your own.

How to upload hardware test scripts

To upload a hardware testing script to MAAS, enter the following:

maas $PROFILE node-scripts create name=$SCRIPT_NAME name> \
 script=$PATH_TO_SCRIPT type=testing

Changing the type to commissioning adds the test script to the commissioning process.

You can list all uploaded scripts with the following command:

maas $PROFILE node-scripts read type=testing filters=$TAG

The optional filters argument lets you search for tags assigned to a script, such as using TAG=cpu with the above example.

A script’s metadata, and even the script itself, can be updated from the command line:

maas $PROFILE node-script update \
 $SCRIPT_NAME script=$PATH_TO_SCRIPT comment=$COMMENT

The JSON formatted output to the above command will include ‘history’ dictionary entries, detailing script modification times and associated comments:

"history": [
    {
        "id": 40,
        "created": "Tue, 12 Sep 2017 12:12:08 -0000",
        "comment": "Updated version"
    },
    {
        "id": 34,
        "created": "Fri, 08 Sep 2017 17:07:46 -0000",
        "comment": null
    }
]

MAAS keeps a history of all uploaded script versions, allowing you to easily revert to a previous version using the id of the version you wish to revert to:

maas $PROFILE node-script revert $SCRIPT_NAME to=$VERSION_ID

Warning: The history for later modifications will be lost when reverting to an earlier version of the script.

To download a script, enter the following:

maas $PROFILE node-script download $SCRIPT_NAME > $LOCAL_FILENAME

To delete a script, use delete:

maas $PROFILE node-script delete $SCRIPT_NAME

How to use tags to group commissioning and testing scripts

Tags make scripts easier to manage; grouping scripts together for commissioning and testing, for example:

maas $PROFILE node-script add-tag $SCRIPT_NAME tag=$TAG
maas $PROFILE node-script remove-tag $SCRIPT_NAME tag=$TAG

MAAS runs all commissioning scripts by default. However, you can select which custom scripts to run during commissioning by name or tag:

maas $PROFILE machine commission \
 commissioning_scripts=$SCRIPT_NAME,$SCRIPT_TAG

You can also select which testing scripts to run by name or tag:

maas $PROFILE machine commission \
 testing_scripts=$SCRIPT_NAME,$SCRIPT_TAG

Any testing scripts tagged with commissioning will also run during commissioning.

How to view testing results

The command line allows you to not only view the current script’s progress but also retrieve the verbatim output from any previous runs too.

If you only want to see the latest or currently-running result, you can use current-commissioning, current-testing, or current-installation instead of an id:

maas $PROFILE node-script-result read $SYSTEM_ID $RESULTS

You can also limit which results are returned by type (commissioning, testing, or installation), script name, or script run:

maas $PROFILE node-script-results read \
 $SYSTEM_ID type=$SCRIPT_TYPE filters=$SCRIPT_NAME,$TAGS

You can also suppress failed results, which is useful if you want to ignore a known failure:

maas $PROFILE node-script-results update \
 $SYSTEM_ID type=$SCRIPT_TYPE filters=$SCRIPT_NAME,$TAGS suppressed=$SUPPRESSED

where $SUPPRESSED is either True or False. The JSON formatted output to the above command will include ‘results’ dictionary with an entry for suppressed:

"results": [
    {
        "id": 21,
        "created": "Tue, 02 Apr 2019 17:00:36 -0000",
        "updated": "Tue, 02 Apr 2019 20:56:41 -0000",
        "name": "smartctl-validate",
        "status": 5,
        "status_name": "Aborted",
        "exit_status": null,
        "started": "Tue, 02 Apr 2019 20:56:41 -0000",
        "ended": "Tue, 02 Apr 2019 20:56:41 -0000",
        "runtime": "0:00:00",
        "starttime": 1554238601.765214,
        "endtime": 1554238601.765214,
        "estimated_runtime": "0:00:00",
        "parameters": {
            "storage": {
                "argument_format": "{path}",
                "type": "storage",
                "value": {
                    "id_path": "/dev/vda",
                    "model": "",
                    "name": "sda",
                    "physical_blockdevice_id": 1,
                    "serial": ""
                }
            }
        },
        "script_id": 1,
        "script_revision_id": null,
        "suppressed": true
    }
]

Finally, results can be downloaded, either to stdout, stderr, as combined output or as a tar.xz:

maas $PROFILE node-script-result download $SYSTEM_ID $RUN_ID output=all \
 filetype=tar.xz > $LOCAL_FILENAME

$RUN_ID is labelled id in the verbose result output.

MAAS can check whether links are connected or disconnected, so that you can detect unplugged cables. If you are not running MAAS 2.7 or higher, you must first upgrade and then recommission your machines to find disconnected links. MAAS not only reports unplugged cables, but also gives a warning when trying to configure a disconnected interface. In addition, administrators can change the cable connection status after manually resolving the issue.

When MAAS detects a broken network link, users will see a screen similar to this one:

If you’re already using a version of MAAS less than 2.7, you will want to upgrade and recommission your existing machines to check link status. Note that you will also receive a warning from MAAS when trying to configure a disconnected interface.

To check network testing results, enter the following command:

maas $PROFILE interfaces read $SYSTEM_ID \
| jq -r '(["LINK_NAME","LINK_CONNECTED?","LINK_SPEED", "I/F_SPEED"]
| (., map(length*"-"))), (.[] | [.name, .link_connected, .link_speed, .interface_speed])
| @tsv' | column -t

which produces an output similar to this:

LINK_NAME  LINK_CONNECTED?  LINK_SPEED  I/F_SPEED
---------  ---------------  ----------  ---------
ens3       false            -           1 Gpbs

From this screen, you can see that the ens3 link is not connected (hence an unreported link speed).

Once you have manually repaired the broken connection, an administrator can change cable connection status:

maas $PROFILE interface update $SYSTEM_ID $INTERFACE_ID link_connected=true

As servers and hardware get faster, the chances increase that you might encounter a speed mismatch when connecting your NIC to a network device. MAAS can warn you if your interface is connected to a link slower than what the interface supports, by automatically detecting link and interface speed and reporting them via the UI:

Depending on your physical hardware, the problem may not be repairable, but once you identify a slow link, you can replace a slow switch without recommissioning.

As servers and hardware get faster, the chances increase that you might encounter a speed mismatch when connecting your NIC to a network device. MAAS can warn you if your interface is connected to a link slower than what the interface supports, when you run the above command:

maas $PROFILE interfaces read $SYSTEM_ID \
| jq -r '(["LINK_NAME","LINK_CONNECTED?","LINK_SPEED", "I/F_SPEED"]
| (., map(length*"-"))), (.[] | [.name, .link_connected, .link_speed, .interface_speed])
| @tsv' | column -t

From the resulting output, you can detect when your link/interface speeds are slower than expected. Depending on your physical hardware, the problem may not be repairable, but once you identify a slow link, you can replace a slow switch without recommissioning.

Administrators can change or update the link and interface speeds after manual changes to the connection:

maas $PROFILE interface update $SYSTEM_ID $INTERFACE_ID link_speed=$NEW_LINK_SPEED \
interface_speed=$NEW_INTERFACE_SPEED

This functionality is only available through the MAAS CLI.

How to configure network validation and testing scripts

MAAS allows you to configure network connectivity testing in a number of ways. If MAAS can’t connect to the rack controller, deployment can’t complete. MAAS can check connectivity to the rack controller and warn you if there’s no link, long before you have to try and debug it. For example, if you can’t connect to your gateway controller, traffic can’t leave your network.

Via the Web UI only, MAAS can check this link and recognise that there’s no connectivity, which alleviates hard-to-detect network issues:

Users can now test their network configuration to check for:

  1. Interfaces which have a broken network configuration
  2. Bonds that are not fully operational
  3. Broken gateways, rack controllers, and Internet links

In addition, MAAS can comprehensively test Internet connectivity testing. You can give a list of URLs or IP addresses to check from the network testing screen:

In addition, MAAS can comprehensively test Internet connectivity testing. You can give a list of URLs or IP addresses to check:

In the ephemeral environment, standard DHCP is still applied, but when network testing runs, MAAS can apply your specific configuration for the duration of the test. While all URLs / IPs are tested with all interfaces, MAAS can test each of your interfaces individually, including breaking apart bonded NICS and testing each side of your redundant interfaces. You can also run different tests on each pass, e.g., a different set of URLs, although each run would be a different testing cycle.

To test individual interfaces, for example, you could issue the following CLI command:

Note that in this command, we are testing internet connectivity to the single interface “br0.”

How to customise network testing

MAAS allow you to customise network testing according to your needs. You can create your own commissioning scripts and tests related to networking, and you can run them during the network testing portion of the MAAS workflow.

There are no particular restrictions on these scripts, so you can test a wide variety of possible conditions and situations. Administrators can upload network tests and test scripts. Administrators can also create tests which accept an interface parameter, or scripts which apply custom network configurations.

Users can specify unique parameters using the API, override machines which fail network testing (allowing their use), and suppress individual failed network tests. Users can also review the health status from all interface tests, even sorting them by interface name and MAC. In addition, MAAS can report the overall status of all interfaces.

How to acquire machines

To acquire/allocate a node with the web UI, select a machine which is in the “Ready” state, and drop down the “Take action” menu:

Select “Acquire” from the drop-down menu, which will bring you to a confirmation screen:

MAAS will acquire the selected machine; you can now find it in the list of “Allocated” machines:

To acquire/allocate a random node:

maas $PROFILE machines allocate

To acquire/allocate a specific node:

maas $PROFILE machines allocate system_id=$SYSTEM_ID

To acquire a node, it must have a status of ‘Ready’.

How to deploy machines

To deploy directly from MAAS, select one or more machine(s) and press the ‘Deploy’ button.

You then have the option of deviating from the default OS, release, and kernel. When ready, press ‘Deploy X machine(s)’ (where ‘X’ is the number of machines selected).

While a machine is deploying its status will change to Deploying to ‘OS’, where ‘OS’ is the name of the OS being deployed (e.g. ‘Deploying to Ubuntu 16.04 LTS’).

Once a machine has finished deploying its status will change to just the name of the OS (e.g. ‘Ubuntu 18.04 LTS’).

To deploy a node:

maas $PROFILE machine deploy $SYSTEM_ID

To deploy a node as a KVM host:

maas $PROFILE machine deploy $SYSTEM_ID install_kvm=True

To deploy with the CLI, the node must have a status of ‘Allocated’. See ‘Acquire a node’ above.

Configure deployment timeout

By default, when you deploy a machine, MAAS will consider the deployment a failure if it doesn’t complete within 30 minutes. You can configure this timeout, if you wish, with the command:

maas $PROFILE maas set-config name=node-timeout value=$NUMBER_OF_MINUTES

How to enlist a machine that’s already running a workload

In order to add machine that’s already running a workload, there are currently two options:

Via the API/CLI, you can create a machine, passing the deployed flag:

$ maas $profile machines create deployed=true hostname=mymachine \   
architecture=amd64 mac_addresses=00:16:3e:df:35:bb power_type=manual

On the machine itself (the recommended way, if the machine is running Ubuntu), you can download a helper script from MAAS and create the machine that way:

$ wget http://$MAAS_IP:5240/MAAS/maas-run-scripts
$ chmod 755 maas-run-scripts
$ ./maas-run-scripts register-machine --hostname mymachine \
 > http://$MAAS_IP:5240/MAAS $MAAS_API_TOKEN

Now you have a machine in MAAS that’s in the deployed state, with no hardware information yet.

How to update hardware information for a deployed machine

The recommended way of updating the hardware information for a deployed machine is to download the maas-run-scripts script and run it on the machine itself:

$ wget http://$MAAS_IP:5240/MAAS/maas-run-scripts
$ chmod 755 maas-run-scripts
$ ./maas-run-scripts report-results --config mymachine-creds.yaml

If you created the machine with the maas-run-scripts, you should have such a mymachine-creds.yaml file already. If not, it should look like this:

reporting:
          maas:
            consumer_key: $CONSUMER_KEY
            endpoint: http://$MAAS_IP:5240/MAAS/metadata/status/$SYSTEM_ID
            token_key: $TOKEN_KEY
            token_secret: $TOKEN_SECRET

You may get the needed credentials from the MAAS API, for example:

$ maas $profile machine get-token wxwwga
Success.
Machine-readable output follows:
{
        "token_key": "Lyy9BS4tKsQakDQScy",
        "token_secret": "V8vta8Azwn6FZVkfHnuTvLGLScAvEufB",
        "consumer_key": "YGT6QKSH65aap4tGnw"
}